expansion tank
Options
Dave_4
Member Posts: 1,404
On a low pressure glycol solar loop (4 lbs static) what should the exp tank pressure be set to.??? Paul
0
Comments
-
Why such a low fill pressure?
with the system pressure dropped charge the tank to the static fill pressure, plus 5 psi.
Remember low fill pressures make air elimination tougher. Solar systems are often charged to 50 psi or more, with a 75 psi relief valve.
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0