Gas pipe sizing

can anyone tell me how many btu's can be delivered with a 3/4" gas line, 500 ft long on 2 lbs. and on 5 lbs?

Comments

  • Mitch_4
    Mitch_4 Member Posts: 955
    here you go

    3/4" Black Iron, 2 PSIG: 448,000...5 PSIG: 705,000

    3/4" Tubing, 2 PSIG: 196,000.... 5 PSIG: 382,000

    All the above based on a 50% max pressure drop.

    Mitch
  • bobbyg_2
    bobbyg_2 Member Posts: 139


    Using the NFGC handbook 1988 it doesn't have 3/4" for 2# OR 5#. Questions to get you an answer:

    1. Is this a straight length, or does it have elbows? You usually add 50% to allow for fittings to make it "equivalent length"

    2. What kind of presure drop do you want. Generally the charts are for 10% pressure drop. (This will affect capacity - more drop = more capacity)