the spray foam is not real good idea because its expansion has "variables". only think, that i have some degree of confidence with is, oil absorption matting with a vapor barrier..the r value is not all that hot though ,so, i would not recommend it as an alternative with all the insulation board options we have these...that basically you will have to file under 'Weezbo creativity' from an age gone by :)

Comments

  • Scott OB
    Scott OB Member Posts: 22
    Under slab insulation

    What would your choice be besides rigid foam for under slab radiant garage heat in the northeast?Any suggests would be appriecated. Scott
  • hot_rod
    hot_rod Member Posts: 24,595
    Not many

    if you want an R-5 to R-10 you need 1 or 2" of foam. NW Foam now has a 3/4" roll foam product, and they may offer a 1" roll out product.

    I did one job where the actually spray foamed the gravel! Not recommended in my opinion. Very un-even and $$$.

    You definitally want 1-1/2 or 2" of foam around the edge and at least 4 feet of the perimeter.

    You may chose to use a roll product for the rest. A lot depends on the subgrade material, and the conductivity of it. Loose washed gravel (pea gravel) is a poor conductor. Solid rock or clay would require a good r value.

    Thre product you choose needs to have the proper psi rating, be waterproof, listed for underslab installation, and ideally... insect proof :)

    hot rod
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Richard_6
    Richard_6 Member Posts: 22
    Please Check out...

    www.crete-heat.com
  • Scott OB
    Scott OB Member Posts: 22
    Crete Heat

    Thanks for every ones info.The Crete Heat looks like something I would like to use.