Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Boiler sizing dilemma

David Nadle
Member Posts: 624
I'm trying to find a replacement boiler. I've measured the radiators at 280 ft^2. My old boiler is rated at 300 ft^2 and has a 5" flue.
Before I had the idea to replace my boiler I had my chimney lined. They sized it to the present appliances and I got a 5.5" liner.
All the boilers I can find today with 5" flues are a bit undersized, ranging from about 1% to 8% less than 280 ft^2.
The Burnham I liked is about 3% under. Presuming that I will insulate the mains, would you say I can get away with it or do I need to take steps to fit a boiler the next size up?
Before I had the idea to replace my boiler I had my chimney lined. They sized it to the present appliances and I got a 5.5" liner.
All the boilers I can find today with 5" flues are a bit undersized, ranging from about 1% to 8% less than 280 ft^2.
The Burnham I liked is about 3% under. Presuming that I will insulate the mains, would you say I can get away with it or do I need to take steps to fit a boiler the next size up?
0
Comments
-
Hmmm 5" is small . .is this a new construction?0 -
Replacement of 30+ year old steam boiler
Not new construction. Sorry if I wasn't clear.0
This discussion has been closed.
Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 110 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 980 Plumbing
- 6.3K Radiant Heating
- 387 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements