Boiler sizing dilemma
David Nadle
Member Posts: 624
I'm trying to find a replacement boiler. I've measured the radiators at 280 ft^2. My old boiler is rated at 300 ft^2 and has a 5" flue.
Before I had the idea to replace my boiler I had my chimney lined. They sized it to the present appliances and I got a 5.5" liner.
All the boilers I can find today with 5" flues are a bit undersized, ranging from about 1% to 8% less than 280 ft^2.
The Burnham I liked is about 3% under. Presuming that I will insulate the mains, would you say I can get away with it or do I need to take steps to fit a boiler the next size up?
Before I had the idea to replace my boiler I had my chimney lined. They sized it to the present appliances and I got a 5.5" liner.
All the boilers I can find today with 5" flues are a bit undersized, ranging from about 1% to 8% less than 280 ft^2.
The Burnham I liked is about 3% under. Presuming that I will insulate the mains, would you say I can get away with it or do I need to take steps to fit a boiler the next size up?
0
Comments
-
Hmmm 5" is small . .is this a new construction?0 -
Replacement of 30+ year old steam boiler
Not new construction. Sorry if I wasn't clear.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements