Steam vs Hot Water

BRIANJ
BRIANJ Member Posts: 118
Can anyone tell me why EDR is the same for Steam and Hot Water if Steam is at 212 and water is 180?

Thanks Brian

Comments

  • Ted_4
    Ted_4 Member Posts: 86
    EDR

    EDR refers to the size in square feet of the radiant surface, not the heat output. Heat output for a given EDR varies according to the operating temperature. One square foot of radiation in a steam system puts out about 240 btu per hour. In a water system at 170 degrees, one square foot puts out about 150 btu per hour.
  • Noel
    Noel Member Posts: 177
    It isn't

    The square feet of surface area is the same (EDR) number, but the output is 240 BTUH per sq.ft. of EDR at 212° F., and 170 BTUH per sq. ft. of EDR at 180° F.

    Noel
  • BRIANJ
    BRIANJ Member Posts: 118
    Steam vs Hot Water

    Ted and Noel, Thanks for your help in explaining this to me. I appreciate your replying so quickly. Thanks again.
    Brian