Water loged Expansion Tank

Jeff Elston
Member Posts: 289
Good Day Gents,
I typically work on boiler rooms in apartment buildings. And I would like to explore the causes for a horizontal ceiling mounted non bladder expansion tank to water log, meaning that there is no air in the top of the tank to provide the needed expansion. If we assume there are no air leaks in the tank. And the tank being empty at the start of things. And the pipe connects to the bottom. Where dose the air go?
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=405&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
I typically work on boiler rooms in apartment buildings. And I would like to explore the causes for a horizontal ceiling mounted non bladder expansion tank to water log, meaning that there is no air in the top of the tank to provide the needed expansion. If we assume there are no air leaks in the tank. And the tank being empty at the start of things. And the pipe connects to the bottom. Where dose the air go?
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=405&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
air
Are there any automatic can vents? 400-3's or 700's or 67's? I had one just today, steel tank and one of the rocket scientists I work with had 3 vents on the system. I removed them and replaced with a coin vent and 1/8" plugs.0 -
vents
there could, be but nothing unusual just one on the air scoop,
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
0
-
air scoop
You don't want to "vent" any of the air, you want to put it back into the expansion tank.0 -
Thank you
I have read that before, just could not remember where.
I do believe this is what is happening. And it is what i told the customer.
I just wanted any other theories that are out there.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
do yourself a favor
Leave a note on the system that explains why you have removed the air vent. That way any tech's in the future who do not have the knowledge will at least leave it alone...0 -
I can only assume.......
.....there is no tank valve to prevent the air from being absorbed into the cooler water and taken back down to the system where it releases it's entrained air after it is heated. Install a tank valve, remove any automatic venting devices and the issue will go away.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 940 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements