Viessmann Vitodens venting specs for fire wall

GW
GW Member Posts: 4,930
Brad,

I'm wanting to pass througha two-hour ceiling. It's hard to explain the exact situation. I'll see if I can get the PE to go along with it. Thanks, GW
Gary Wilson
Wilson Services, Inc
Northampton, MA
gary@wilsonph.com

Comments

  • GW
    GW Member Posts: 4,930
    gotta pass through a two-hour

    does anyone know where in the specs it specs out the metal/material for the vent piping? I need to dot I's and cross T's... new construction commercial job.

    Thanks, Gary
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • Brad White
    Brad White Member Posts: 2,399
    NFPA-90A

    allows steel sheetmetal to account for a one-hour rating by default although not explicitly. The reason is that a one-hour partition can have a continuously duct pass through it without a fire damper. A transfer duct would have a damper. 1.5 hour ratings and up you need a damper. Not applicable to your venting situation, just some background.

    I would enclose it after testing in a continuous 2-hour enclosure, essentially extending the partition rating along the vent system. You could also use Pabco or Fyre-Wrap (which everyone says is expensive but nobody tells you the price :)

    We used Fyre-Wrap on a smoke control system to protect the fan and dampers as it passed from the enclosure to the outside.