F05 Investigation
On Friday August 2nd, in an effort to assist the installing contractor, John Sawyer of Heat Transfer Products visited the job site mentioned in a previous post (See Munchkin F05).
John thoroughly reviewed the installation; the piping was an excellent representation of a parallel primary/secondary set up. Even if not as specified by our manual, it was found that the circulator sizing was not the issue. The way this was determined was by looking at the inlet and outlet temperature from the boilers status menu, and they could then see the temperature differance was well within a range that John was comfortable with. A review of the fault history on the installation was done through Johns laptop, and he found only the 4 F05 (high temp) codes.
What was found to be the most likely issue was the possibility that DHW circuit of the Vision 1 installation was able to trap air. The contractor resolved this with the installation of an additional air elimination device. The other issue that was looked at was the possibility that the internal flow check in the circulator on the boiler loop was stuck open; if this were to happen, the DHW circulator would pump through the boiler loop, pump through the closely spaced tees on the primary loop and back through the coil on the indirect, bypassing the boiler. The check was removed, cleaned and returned to its original location to hopefully eliminate this as a possibility.
I just wanted to let you know the possible cause, and the fix.
Chuck Shaw
Heat Transfer Products0 -
I'm Impressed
Very admirable of HTP to step to the plate and proactively work to solve the home owner's difficulty. Can't ask for better factory support. (BTW I'm a home owner, so I don't have any axe to grind here)0 -
Ah
> On Friday August 2nd, in an effort to assist the
> installing contractor, John Sawyer of Heat
> Transfer Products visited the job site mentioned
> in a previous post (See Munchkin F05).
>
> John
> thoroughly reviewed the installation; the piping
> was an excellent representation of a parallel
> primary/secondary set up. It was found that the
> circulator sizing was not an issue. The way this
> was determined was by looking at the inlet and
> outlet temperature from the boilers status menu,
> and they could then see the temperature
> differance was well within a range that John was
> comfortable with. A review of the fault history
> on the installation was done through Johns
> laptop, and he found only the 4 F05 (high temp)
> codes.
>
> What was found to be the most likely
> issue was the possibility that DHW circuit of the
> Vision 1 installation was able to trap air. The
> contractor resolved this with the installation of
> an additional air elimination device. The other
> issue that was looked at was the possibility that
> the internal flow check in the circulator on the
> boiler loop was stuck open; if this were to
> happen, the DHW circulator would pump through the
> boiler loop, pump through the closely spaced tees
> on the primary loop and back through the coil on
> the indirect, bypassing the boiler. The check
> was removed, cleaned and returned to its original
> location to hopefully eliminate this as a
> possibility.
>
> I just wanted to let you know the
> possible cause, and the fix.
>
> Chuck Shaw Heat
> Transfer Products
0 -
Ah yes!
Nothing like a hands/eyes on visit with consideration given to the fact that the devil is often in the details. Nice work!0 -
HTP
Ah what it's all about. HTP has been there for me every time they been needed.0 -
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements