OLD Oil Boiler & Burner- Replace or Not
Steamhead (in transit)
Member Posts: 6,688
and the Beckett is the model AF, it could be problematic. That boiler runs much better with a higher-static burner such as the Beckett AFG, Carlin EZ or Riello. With the AF, a 68 series boiler can plug up with soot since the flue passages are so small.
If that were my house, I'd put in a MegaSteam.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
If that were my house, I'd put in a MegaSteam.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
OLD Oil Boiler & Burner- Replace or Not
I have a Weil McLain Boiler from 1984 and Becket burner. My oil man is saying that it is time to replace the unit.Gas Water heater.
The readings are as follows: Done 10-06
FT- 553.6 CO2- 9.7%
02- 7.9% x - 62.6%
n - 79.9% draft- -0.05 inH20
CO- 59ppm COud- 95ppm
AT- 70.01 F
Does this information tell you anything about the condition of the system other than the age?0 -
We'd need to know more
what model is it (may be shown as "size", may end in 66 or 68)? Is it a steam or hot-water system? Is the boiler considerably oversized?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
OLD Oil Boiler & Burner- Replace or Not
Steamhead,
I checked and found only one label Weil McLean #CP1017919
SIZE: 20"lx13.5"wx34"h
Steam system
I do not know if it is oversized?0 -
Oversized
I never meet a 1984 boiler that was not oversized0 -
How about
taking a pic and posting it here?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
1984 Boiler
I had the oil guy recently quote a HB Smith Series 8 three section, cast iron steam boiler pkgd w/ an AFG Beckett oil burner, steam pressuretrol, probe style low water cutoff, automatic steam boiler feeder, pressure relief valve to replace the 1984 boiler and burner. What do you think.0 -
Old 1984 Boiler
Picture attached0 -
Old 1984 Boiler
> taking a pic and posting it here?
>
> _A
> HREF="http://www.heatinghelp.com/getListed.cfm?id=
> 367&Step=30"_To Learn More About This
> Professional, Click Here to Visit Their Ad in
> "Find A Professional"_/A_
0 -
Old 1984 Boiler
0 -
Old 1984 Boiler
0 -
Old Boiler/Burner
Looked up some of my "ancient" literature to find from your given dimensions that your unit is most likely to be a Model 468 or 468V (depends on back flue connection or vertical flue connection). That being said, the unit is rated at 465 Sq.ft. EDR. To see if it is oversized measure up the radiators connected to the system and find out if they match this EDR then, "rule of thumb" at the time this unit was installed was to add to the radiator "load" an additional 33% for piping & pick up losses. The boiler rating should NOT exceed this amount by more than 5-7% of the "combined" load.
From the combustion analisis figures you posted your unit is running within reason for it's age but could do better. Section sealing (on the fireside) would be a good idea as well as replacing the insulation in the front panel, and the target wall. Your draft over fire is also too high and this is a contributing factor to the high flue gas exit temperatures. Your burner is a flame retention head unit of the first order. A new burner would be (only if properly installed, adjusted, and maintained) more fuel efficient.
There is a lot more that can be done to enhance the efficiency of this "old" beast, but not here.There was an error rendering this rich post.
0 -
BNL
did a study on the % fuel savings when replacing older equipment. Replacing a 20+ year old pin type oil boiler with the same type new boiler yielded about a 16 % reduction in fuel usage.These were hot water boilers not steam.
I would have to think a properly sized Megasteam and indirect would yield at least that much if not more
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements