flueway condensation

Steve_153
Member Posts: 4
I'm bidding a replacement for a Weil-McLain P368 steam boiler. This unit was installed less than 10 years ago. It has plugged due to condensation no less than 5 times. The unit is fired at full capacity, has great draft, is always set up with instruments, and is in a dry basement. The unit is properly sized for the connected load is piped properly and doesn't surge. There are no signs of leaks in the sections or at the gaskets. The boiler doesn't use excessive water. It almost seems like the iron is porous. Is that possible?
0
Comments
-
Try
a L4006A to maintain a little temp during heating season,clean the boiler thoroughly immediately after heating season and before summer shutdown. This usually does the trick
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
This model
This model and the Peerless JOT are the worst for condensing as you describe. The fix is keeping them warm. The Peerless I could never figure why but the Weil I always figured it was from having gaskets between the sections.
Leo0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 68 Pipe Deterioration
- 940 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements