expansion

john_177
Member Posts: 3
I'm a mechanical contractor in Colorado. The reason I'm emailing you is to see if you could help me with an expansion problem. What I have is an array of 30 flat plate collectors in a field. It is approximately 200 feet from the mechanical room to the collectors. I ran 2 " copper both to the collectors and from them (supply, return). I know that the copper will expand about 3 to 5 inches on each run. How do I account for this? My supplier can't find 2" expansion joints and what they recommended was braided flexes, but I don't see flexes accounting for 4 inches of expansion. My other option is loops of 2" soft copper in the ground and build insulated boxes to allow for the expansion, but this doesn't feel very professional and I don't know what kinds of velocity problems this could cause on the pipe because I have a 5 horse pump moving the glycol mix.
Anything would help thanks
john
Anything would help thanks
john
0
Comments
-
exp.
In the past I have used 4 circular loops of 1" pex to equal the volume and flow of 2" copper. This can be done fairly compactly, but you would be limited to 200 F max. system temperature due to the pex.0 -
Metraflex
http://www.metraflex.com/
They have a line of nice flexible "hairpins" as well as in-line devices which make compensation a snap. All materials and joint methods too."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0 -
Off Set
You off set the braided flex from line of run and use one on each end .0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements