HWH riser vents
automatic air vents available, I use these <A HREF="http://customer.honeywell.com/honeywell/ProductInfo.aspx/EA122A1002"> H/B vents </A> , and a Q122A1001 "safe waste connector" can be added to pipe-it to a safer drainage point. But <b>remember</b> , adding any auto-vent to an area where positive pressure is <i>not maintained</i> WILL allow them to "suck" more air into the system also. <BR><BR>Dave
  • D. R. Riddle
    D. R. Riddle Member Posts: 3
    automatic vent that would not damage apartment
    We're encountering trapped air in the top floor circuits of hot water heating systems. In a couple of cases the owner vents the air manually to get a couple of days worth circulation. I wanted to install a regular small vent such as we use to vent the boiler itself but I'm concerned about water damage to the room. What is a good quality vent that is suitable for this application ? Although other factors are causing the problem I feel like a vent on the top is a good extra.
  • D. R. Riddle
    Venting at top of risers.
    I believe you've answered my question as to why top riser vents are'nt used. The risers of subject top out a good 50 feet over the boiler. The hwh circulator does not operate constantly.
  • Brad White
    Brad White Member Posts: 2,399
    Treating the Symptom
    Not the disease, I suspect.
    As Dave noted, any vent without pressure can breathe both ways. You did note "other causes", so let's make sure that you are:
    1) Pumping away from your expansion tank.
    2) Have adequate pressure in your system (about 4 psig at the top plus another 0.433 lbs. for every foot of height.
    3) A good air separator is an option at the boiler and upstream of the circulator. Once you get the air out this should not be necessary.
    Do at least #1 and #2 above and you should not have to add vents or at least use them more than twice.
    My $0.02
    Brad
    -Ernie White, my Dad
  • Steamhead (in transit)
    Steamhead (in transit) Member Posts: 6,688
    And
    the system should be set up to "pump away" from the air separator/tank connection.
    Then kiss your air problems goodbye.