HWH riser vents
automatic air vents available, I use these <A HREF="http://customer.honeywell.com/honeywell/ProductInfo.aspx/EA122A1002"> H/B vents </A> , and a Q122A1001 "safe waste connector" can be added to pipe-it to a safer drainage point. But <b>remember</b> , adding any auto-vent to an area where positive pressure is <i>not maintained</i> WILL allow them to "suck" more air into the system also. <BR><BR>Dave
0
Comments
-
automatic vent that would not damage apartment
We're encountering trapped air in the top floor circuits of hot water heating systems. In a couple of cases the owner vents the air manually to get a couple of days worth circulation. I wanted to install a regular small vent such as we use to vent the boiler itself but I'm concerned about water damage to the room. What is a good quality vent that is suitable for this application ? Although other factors are causing the problem I feel like a vent on the top is a good extra.0 -
Venting at top of risers.
I believe you've answered my question as to why top riser vents are'nt used. The risers of subject top out a good 50 feet over the boiler. The hwh circulator does not operate constantly.
Thanks0 -
Treating the Symptom
Not the disease, I suspect.
As Dave noted, any vent without pressure can breathe both ways. You did note "other causes", so let's make sure that you are:
1) Pumping away from your expansion tank.
2) Have adequate pressure in your system (about 4 psig at the top plus another 0.433 lbs. for every foot of height.
3) A good air separator is an option at the boiler and upstream of the circulator. Once you get the air out this should not be necessary.
Do at least #1 and #2 above and you should not have to add vents or at least use them more than twice.
My $0.02
Brad"If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0 -
And
the system should be set up to "pump away" from the air separator/tank connection.
Then kiss your air problems goodbye.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements