Hydronic air handler or Modulating furnace
jp_2
Member Posts: 1,935
possibly the furnace. everytime you change mediums you lose efficiency. heat water to heat air opposed to heating air somewhat directly, both systems heat a heat exchanger first.
but i agree with brad too.
but i agree with brad too.
0
Comments
-
hydronic air handler
What would be the most efficient?
a new modulation furnace both flame and cfm, or
a hydronic air handler supplied by a Pinnacle boiler
with outdoor reset.
currently I have two furnaces one for the first floor, one for the second, the heat loss is just over 130,000btu,
which is why i was considering the air handler but can not
find any info on how efficient the system will be if the boiler modulates but the blower does not.
Walt0 -
Things to think about...
Good question and I really do not have an answer but this is the methodology I would use to help sort it out:
1) One point of combustion versus two: the compounding of inefficiencies. Can you run the Pinnacle down less than the modulating range of any one furnace?
2) Will the two zones run together much of the time? In other words can they both enjoy a turn-down within the modulating range of the boiler? Say both are running intermittently on a 30 degree day and the boiler is modulating near 30 percent, allowing more constant burns?
3) Cost of electricity to run the fans: Hours at what kW draw?
3A) Who says you cannot modulate a Hydro Air AHU and have the best of both?
I guess it depends on the real-time efficiency of the furnaces (and two points of maintenance but also some redundancy should one fail) compared to a hydro air system where you can vary the distribution side a bit.
Not a full answer by any means, just some random drive-by thinking."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0 -
Unless there has been a recent new introduction, the Rheem Presitige series furnace is the only one I know of that combines a nearly (something like 60? steps) modulating burner with a variable-speed (far fewer steps) blower and most importantly an integrated thermostatic controller. By combining variable burner output with variable delivery of heat and a controller that understands how to make these things work together, it is essentially the Vitodens of forced air furnaces...
While the Rheem is fairly new I find no web evidence of it being a disaster like the Lennox "Complete Heat". Providing it's available in the appropriate sizes and budget allows, I'd choose that over hydro-air.
Why?
While Brad is quite right that there's no reason a mod-con (using reset) cannot drive multiple air handlers there are some serious complications. Unless the air handlers are variable speed (and regardless of how generously their heat exchangers are sized) you won't be able to have much slope in the reset curve unless the air handlers are also variable speed.
Unless I've missed something there are no thermostatic controllers that understand how to make a mod-con "talk" to a variable speed air handler and vice-versa. Such is a true requirement if the highest comfort and efficiency are your goals.
With any variable speed air-handler I believe it doubly important that your returns are FULLY DUCTED AND ABUNDANT!!!
If you do use hydro-air and also use a mod-con boiler, and combine this with daily setback, please, please, please use "smart recovery" thermostats set such that space temperature is FULLY RECOVERED BEFORE MORNING SHOWERS!!!!!0 -
Mike.....
I am not sure why you say you cannot have much slope for an air handler. I have some running full reset and have been that way for decades. Tekmars reset curve for air handlers is nearly a straight line....no curve, since the output of an air handler at constant air flow is quite linear to the temperature of the water.
Boilerpro
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Cannot Have Much Slope...
...and "nearly a straight line + no curve" are the same thing.0 -
I want to thank eveyone that has responded
I had all the plans to turn this house into a hot water,radiant home and utilize the duct work for summer a/c and air exchange , then the loss of space for equiptment bothered me. that is the time i considered the air handler
must of your ideas are the same that i came up with' plus a few more which led me to post my delema.
as for a full modulating furnace, flame and blower,LUXAIRE
has had alot of success with there new model FL9C
this is a spring project so i have all heat season to decide
any other ideas please throw them this way
thanks
W0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements