Potentially cold

Tony_23
Member Posts: 1,033
Went to a new build yesterday. TG it's not finished.
"Plates", the style of which are made of flashing. 1/2" tubing installed by HO threaded thru holes 1" or smaller, drilled so close to the top of the joists they look like they're notches, not holes. Loops are 300' +/- 15 %.
The best part is the Great Room. Windows facing due South, .30 U-factor, the whole wall close to 400 sq.ft. of glass. 400 sq ft of floor that somehow is supposed to emit 35 BTU/sqft. 8" centers. 143* water, 20*DT. Also, 1800 ft of tubing is supposed to be magically crammed into 400 sqft of floor and on 8" centers to boot ! It IS a tile floor, but I really don't think so :)
Oh yeah, it was to be insulated from below with the magical reflective qualities of dbl bubble foil, period :)
And we wonder how radiant gets a bad name.........
"Plates", the style of which are made of flashing. 1/2" tubing installed by HO threaded thru holes 1" or smaller, drilled so close to the top of the joists they look like they're notches, not holes. Loops are 300' +/- 15 %.
The best part is the Great Room. Windows facing due South, .30 U-factor, the whole wall close to 400 sq.ft. of glass. 400 sq ft of floor that somehow is supposed to emit 35 BTU/sqft. 8" centers. 143* water, 20*DT. Also, 1800 ft of tubing is supposed to be magically crammed into 400 sqft of floor and on 8" centers to boot ! It IS a tile floor, but I really don't think so :)
Oh yeah, it was to be insulated from below with the magical reflective qualities of dbl bubble foil, period :)
And we wonder how radiant gets a bad name.........
0
Comments
-
but
you forgot to mention that they are adding a Tom Swift jr and his atomic radiant heat magnifyer for those really cold days...0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 940 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements