tepid zone off a Munchkin boiler
S R Denny
Member Posts: 26
In a new greenhouse which will be heated by a Munchkin thru radiators (by others), I've been asked to run a second zone to a small SuperStor tank set to warm water to 70-80ºF for irrigation purposes. The gardners say winter tap water is too cold for their tropical plants. Anyone foresee any problems with this idea?
0
Comments
-
Not a problem
as long as the aquastat controlling it will go that low?
The Vision package for the Munchkin allows for DHW via a thermistor, in lieu of a tank aquastat. 95- 160F if I'm not mistaken.
Another option would be a mix valve on the tank DHW outlet. This would allow you to keep the tank temp higher (above legionella temperatures and mix down to the required temperature. more DHW output also with a higher tank temperature.
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Hot Rods got a good point.
especially since they will be spraying (atomizing) that legionella water..
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Right after I started this thread I saw an add for Leonard Temperature Controls with the heading "More Tepid Choices..."
I think they've got just what I'm looking for.
Do you think I could go directly off the boiler or would a tank be necessary?0 -
stick w/ the superstor...
and the mixing valve. It will be easier and will last longer. Running fresh water through the boiler all the time might lead to scale build up in the boiler...kpc0 -
Depending on the gpm flow required
you might get a flash HX or even a flat plat exchanger. Some of the mod cons offer flat plate or small tanks as an option. Laars Mascot, MZ and a few others.
I've used that small Triangle Tube Smart heat exchanger to do instantanous HW production, off a small Prestige mod con.
Everhot is another brand of small DHW generators.
At those low temperatures you should be able to supply 3 gpm easily, even with a mere 100K input, depending on incoming water temperatures, of course. Really no need for a storage tank if you generate the DHW as needed.
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements