Depth of pipe
Bryan_16
Member Posts: 262
Looking at puttting tubing in an 8" thick concrete slab. Normally I tie the tube to mesh or staple it to the foam. Reaction time will be slower if I put the tube at the bottom of the slab, but how do I get the tube to stay in the middle?
0
Comments
-
Either do ....
2 pours...4" then pex then 4" or use chairs...Chairs are wire mesh supports that raise the tubing up into the middle of the slab...kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
thick pours
Here's two photo's of the BCIT Aerospace Hangar to illustrate whats been said above.0