Dropped Header Question
Is there a minimum that the dropped header needs to be above the waterline in the boiler?0 -
The risers from the boiler
typically need to be 24 inches at minimum above the maximum permitted boiler waterline, and I'd go higher if possible. This is to help keep water from reaching the header.
The header itself can be lower than that, I'd keep it maybe a foot above the waterline.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
drop
> Is there a minimum that the dropped header needs
> to be above the waterline in the boiler?
I have dropped several to almost the top of the jacket with excellent results.first bring riser up to required dimension.0 -
Thanks
I was thinking that it was not that big an issue, but wanted to make sure. I did my first dropped header last winter, took a lot of convincing of the boss but he finally caved in, yesterday he said we got another header to replace and I think you better try that thing you did last time it worked out great. I will have 2 24 inch risers out of the boiler and dropping about six inches so the risers have close to 30" to the waterline and the header should be about 20" above the waterline. This is on a five or six section 8 series Smith that was installed 5 plus years ago with one riser made from copper. Thank you Bob and Frank.0 -
Dropped Headers
As we now show in our Megasteam I&O manual and as indicated already by others, that vertical rise from the NWL needs to be at least 24". Hope this helps.
Glenn Stanton
Manager of Technical Development
Burnham Hydronics
U.S. Boiler Co., Inc.0 -
Dropped header height
As we show in our Megasteam I&O manual and as already indicated by others, that vertical rise needs to be at least 24" from the NWL of the boiler. Hope this helps.
Glenn Stanton
Manager of Technical Development
Burnham Hydronics
U.S. Boiler Co., Inc.0 -
Take your camera with you
we'd love to see before-and-after pics!
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Thank You Glenn
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements