Galvanic Corrosion Contrl

Bruce Stevens
Member Posts: 133
say it is not needed, it is a great way to make the transition.
0
Comments
-
Galvanic Corrosion Control
Can the transition from steel to copper tube in a hot water heating system be made with a brass valve at the branches? Steel to brass to copper?0 -
Is this method of protection as good as a dialetric nipple or union.0 -
Thanks Can you tell me where in piping literature that using a brass valve between steel pipe and copper tube i a heating system is an effective form of galvanic control.0 -
if you go to www.copper.org
you can find all sorts of reading material on this subject. Everything from a basic galvanic chart to PHD authored case studies.
Basically in a closed loop, sealed system once the O2 is out corrosion cannot occur, regardless of the "blend" of materials used.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
oxygen
Oxygen has nothing to do with electrolysis. Oxygen is responsible for oxidation (rust.) Corrosion due to dissimilar metals is electrolysis and is more related to the water PH. A lack of oxygen will not stop galvanic related damage to one of the dissimilar metals in a closed loop!
Pete0 -
Galvanic Corrosion Control
>Corrosion due to dissimilar metals is electrolysis and is more related to the water PH.
True, but galvanic corrosion produces oxygen.
SFAIK, galvanic corrosion occurs between dissimilar metals which are immersed in a suitable electrolyte. You will get a small current flowing through the water and through the metals. The galvanic current splits the water into oxygen and hydrogen. The oxygen dissolves in the water and corrodes the steel components.
The hydrogen is usually discharged from an air vent, or it appears at a radiator air vent, from where it can be collected in a jar and ignited to prove that galvanic corrosion is happening.
In a heating system, the best solution is to make sure the water isn't a suitable electrolyte by adding an inhibitor. Most inhibitors make the water alkaline ( pH 8 or 9). You don't need brass couplers or dielectric unions in a heating system.
If the water is acidic (pH<7) it will encourage galvanic corrosion. The usual cause of acidic water is active soldering flux residues which hasn't been flushed out, anti-freeze that has degraded and/or neglect of the corrosion inhibitors.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 68 Pipe Deterioration
- 940 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements