Plastic Piping in Steam System
Rob Pickard
Member Posts: 20
I noticed that my 6-story condo building has sections of plastic pipe that are used as part of the water return line for the two-pipe steam system. It appears that these were added at some point to replace the metal ones that had been used.
Should I recommend that these plastic pipes be replaced, or are they fine because they should only be carrying hot water back to the boiler?
Should I recommend that these plastic pipes be replaced, or are they fine because they should only be carrying hot water back to the boiler?
0
Comments
-
Wow!
That's a no-no. I suppose CPVC MIGHT tolerate over 200 degrees F - which would be common for a steam return, but here's what they wrote in their specs.
"USES/APPLICATIONS
CPVC piping which is suitable for hot and cold water distribution has a 400 psi pressure rating at room temperature, and a 100 psi pressure rating at 180 F."
I suspect any sort of insurance or municipal inspection would result in a "red" tag failure notice and an order to stop using the system unti,l repairs are made. The obvious use of plastic in a steam system is from lack of knowledge, coupled with an errant "save a buck" mentality.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
plastic pipe
What happens when a steam trap fails and passes steam into the plastic pipe?? That WILL happen, I just don't know when. But it will happen in the winter, probably on a Saturday nite in February.....no service man available to replace piping then, shut down the boiler, freeze out the people living there, disrupt the whole building, make enemies out of neighbors, think about it. Get rid of the plastic....that stuff is good for drainage[period]0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements