Btu's of flowing water
Glenn Sossin_2
Glenn Sossin_2 Member Posts: 592
I made this chart up a while back. It should help you. It uses the generic 500 value for water (8.33lbs x 60min/hr)
  • Paul B_5
    Paul B_5 Member Posts: 60
    Flowing water Btu formula
    What are the formulas for lets say a 10,20, or 30 deg temp drop /or temp gain of flowing water at say 1 gpm. Paul
  • Chris_91
    Chris_91 Member Posts: 5
    Q = 500*gpm*delta T
    The 500 is assuming you're pumping 100% water. The number reduces to 490-480 depending on concentration of glycol.
    Delta T in F.
  • ALH_4
    ALH_4 Member Posts: 1,790
    Specific heat
    And the 500 is multiplied by the specific heat of the solution (based on glycol manufacturer supplied numbers). Water is 1 btu/lb-°F. 50% Dowfrost solution is 0.85 btu/lb-°F.
    The 500 comes from water weighing 8.33lb/gal multiplied by 60 min/hour.
  • Dennis10
    Dennis10 Member Posts: 2
    Paul, here's one I use when I need to figure out the flow rate for a zone at variuos delta t's Zone's BTU's divided by 500 divided by the delta T desired = the zone flow rate.
  • Glenn Sossin_2
    wrong attachment
    Sorry attached the wrong file. This is an excel sheet that lets you plug in various flow rates, delta t values, etc.