blown transformer
jim lockard
Member Posts: 1,059
Have you examined the wire at the outside unit, for both dog chews and weed wacker attacks?
Turn power off to both inside and outside units, Placing a small fuse in the low voltage circuit will help preserve xformers. Was the t-stat in cooling or heating? With your Ohm meter start checking low voltage coils til you find the coil that is short to ground. I would check the outdoor contactor coil 1st. Best Wishes J.Lockard
Turn power off to both inside and outside units, Placing a small fuse in the low voltage circuit will help preserve xformers. Was the t-stat in cooling or heating? With your Ohm meter start checking low voltage coils til you find the coil that is short to ground. I would check the outdoor contactor coil 1st. Best Wishes J.Lockard
0
Comments
-
blown transformer
heres the problem. The system is 3 years old and has never had a problem, I have 249v going in and 29 going out and as soon as i hoock up the low volt and turn on the power the transformer burns out.i know there is probably a short on the low volt side but where should i look first and how.0 -
Jim has it right.....
Chasing down a short is an Art and I have see guy's spend countless hours looking and looking and some find the problem fast. Call in a Pro if you have to. Since your short can be ANYWHERE, the system as a whole should be isolated to find out where.0 -
Beside a short
I have also seen x-former fry when mice get into the control box and get debris in the contactor preventing it from pulling in.0 -
go to radio shack...
and buy a lamp holder with a 24v bulb - disconnect one of the leads of the 24v output and put the 24v bulb in-line - it should burn brightly, and wont short out, and now you can go and disconnect section at a time until the bulb burns only half bright indicating a normal load, if it goes out completely then you have disconnected everything and need to back-up now you can easily go step by step and find your short without worrying about a burnout also look where wires go through holes as vibration usually wares them through to the bare metal - this is not rocket science I personally use 2 12v pizo electric horns in series so I can hear it without looking - but dont do it when the HOs are around they dont take well to loud sounds0 -
OR
You could buy tools like a clamp on ammeter and learn how to properly track down shorts.0 -
Go with the bulb kid.
The ampmeter will not limit the short current and the Xtmr will blow again the lightbulb load is a better bet for limiting damage and costs.0 -
Inline fuse with alligator clips attached
Works well too...strangest thing I ever saw in a condensing unit J-box was a baby mouse and small copperhead snake, both fried when they got across the contactor...no joke!, but the only witness to this is no longer with us.0 -
I believe you Mikey
I have found both myself. Only once though. The mouse was skeleton and he bit in one of the wires and grounded itself out. Strange........
Mike T.0 -
blown transformer
you can get at radio shack a 3 amp mini .lo voltage circuit breaker. disconnect the lo- voltage wiring at the furnace or air handler 24v trans.attach one leg of the mini breaker to the R terminal, and the other to the Rwire to the tstat. then as you rewire each other item back in.(with the power off ) as they get wired in. turn the power back on. you will then find your problem. without a need for a bunch of 24v fuses or transformers. OR you could call in a tech to troubleshoot for you0 -
In a short,.....?
All I can say is USE your clamp on ammeter and there will be no need for horns, a trip to Radio Shack, or buying a bulb to do what was mentioned. No disrespect, but are you men kidding me? I guess if it works and you are comfortable,... go for it. I guess to each his own and I am sorry if I ruffled any feathers, but any short can be found in 3 minutes or less with the tried and true clamp on ammeter. Please don't take this the wrong way, but this is one question that I am passionate about.
Peace.......
Mike T.0 -
thanks
thanks for all the great suggestions. I found the prob it was in the contacter coil.0 -
No ruffled feathers here, T
As you say, to each his own. seems like in the old days, a 24v. transformer was..."tougher"? I've seen anticipators fry on T87's before the xmfr. would go. Your clamp-on works for you, but I was taught to do it a different way...More important than tools is the technique, and all of the above will work, but troubleshooting anything requires common sense and a logical sequential approach. Ladder diagrams, which were NOT included with equipment schematics back in "the day" make things a lot easier..you can "see" how each device is powered, and in what order, start to finish. I wish more people in our industry had your passion, and pride in their work. I guess it has something to do with how and by who we were trained by. i've been very fortunate in that regard.0 -
Like my Father said before me:
What the hell are Ya doing with that clamp on meter,....You don't need that!!!:-)
Mike T.0 -
lucky you...
thats a rare one, open coils or fuzed contacts are far more common - as well as abraded through insulation0 -
yep...
a stupid bulb in series with a start or run capacitor will test it fortwith..
off = open - dead
full brightness = shorted - dead
medium brightness - for run type and half brightness for starting type = good0 -
Contactor
Bad contactor on the outside unit as I predicted, not bad for a cyber trouble shoot. Glad you got it fixed. Best Wishes J.Lockard0 -
Brings back memories
That brings back memories of my dearly departed father. He was full of tricks like that.
I, personally, was never a big fan of his tricks.
0 -
so what did you use before...
the "capacetance" range on your DMM ??? - dont tell me you were a "parts changer"0 -
I have been fortunate
I have been fortunate enough to have been raised in the era of digital (at least decent quality analog) meters. I still enjoyed my old man's stories (and lectures) though.
Now I get to lecture others...
0 -
Personally,
I like to replace my burnt transformer with one that has the little breaker built in and then test each circuit separately to see which one blows the breaker. I always replace a bad transformer with one with the little breaker, it just seems like the right way to do it.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements