BTU Formula for Hot Air
Jim Davis_3
Member Posts: 578
The formula for heating is CFM X Delta T X .98 = BTU
The 1.08 multiplier was for cooling and cooler air 45 -55 degrees.
Heating BTU's are for warmer air 120 -140 degrees. The correction or BTU factor for hot air is .98 - .99. Or to keep it simple CFM X Delta T is close enough and you don't need a calculator.
I am looking for a Formula to figure out the BTU's from the cold air in, hot air out and the heat difference multiplied or divided(???) by the CFM's. Thanks for your help.0 -
Btu/Hr = (CFM)(.018)(60 min/hr)(Temperature difference). Plug in the known factors and solve for the unknown. .018 are the Btu's one cubic foot of air will absorb/give up at a one degree temperature difference. Hope this helps.0 -
you are both right...
Remember with water we use times 500 in the deltaT calcs cause btu are in pounds per hour and we deliver it at gallons per minute so 60 minutes, times 8.33 pounds per gallon = 499
Same here:
we deliver it at feet per minute, so .018 per foot pet hour , times 60 minutes = 1.08
OK, but...
What is Delta T?0 -
shorthand for change in temp...
of the heat transfer medium across the load - eg if air is supplied at 110 and returns at 90, then the delta-T is 200
- 114 Geothermal
