broomwell steam valves (vapor)

Leo Grace
Member Posts: 1
1895 victorian home in Massachusetts with 20 antique radiators all with (vapor) Broomwell type shutoff valves (packless). All valves leak steam and boiling water from the tops. CAn they be placed with a more modern alternative? Are modern Pressuetrol sensors indicative of a vacume or pressure system as the boiler has two Honeywell Pressuretrol sensors on it.
0
Comments
-
Those valves can be rebuilt
get in touch with Woody Tunstall at Tunstall Associates, www.tunstall-inc.com . Tell him we sent you.
A Broomell system is designed to run at ounce pressures- typically less than 7 ounces. You need a Vaporstat to control the boiler at these pressures. The usual Pressuretrol won't do.
The dry return was originally vented thru a condensing radiator into the chimney, so the draft would pull air from the system. If this hookup is gone, vent the returns with monster vents such as Gorton #2 units.
"Steamhead"
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements