amtrol heatmaker leak
joe_14
joe_14 Member Posts: 138
sounds like tank is history did it have an st domestic expansion tank
joe g
  • mike t_3
    mike t_3 Member Posts: 6
    amtrol heatmaker leaking
    amtrol heatmaker leaking , foam rubber insulation wet, cannot find a leak at any of the connections. can this tank be saved?
  • kevin coppinger_4
    kevin coppinger_4 Member Posts: 2,124
    does not sound good...
    is it a boiler mate or a hot watermate? How old? kpc
  • Jeff_92
    Jeff_92 Member Posts: 6
    Amtrol BoilerMate
    I assume that there is water leaking from gasket and/or the bolts what the coil bolts into the tank? If that is the case you can feel the steel shell of the tank up around the crown to see if it is hot. If so the internal bottle has failed and the tank needs to be replaced.
    How old is this tank? If the tank is not that old there could be other reason's that this bottle failed early. We normally see life spans on the bottle of 14-24 years with normal ussage
  • mike t_3
    no DHW expansion tank, someleak from vent of DCA back flow preventer, unit is 80 gallon boilermate
  • mike t_3
    no expcnsion tank on DHW line, some leak from vent of DCA backflow preventer, this unit is an 80 gallon boilermate
  • mike t_3
    amrtol heatmaker leak
    this unit is 8 years old