I would say at 170F AWT, under 500 as a base assumption. Possibly 450 or less given that it is recessed (probably not too deep- you need those studs!) and that the air has to take an extra turn before exiting the enclosure.
If this holds true, there would seem to be between 33.75 MBH and 37.5 MBH potential output, corresponding to between 31 and 34 BTUH per SF. In a zero degree design climate, that would seem reasonable to me if the house was insulated and sealed well.
As you note, there is no point in installing more boiler than you have radiation to support, not to mention installing more boiler than you need, period.
Strapping a jet engine on a canary comes to mind :)
If this holds true, there would seem to be between 33.75 MBH and 37.5 MBH potential output, corresponding to between 31 and 34 BTUH per SF. In a zero degree design climate, that would seem reasonable to me if the house was insulated and sealed well.
As you note, there is no point in installing more boiler than you have radiation to support, not to mention installing more boiler than you need, period.
Strapping a jet engine on a canary comes to mind :)
0
Comments
-
went to look at a house yesterday
kinda of an independant review...noisy operation, high gas bills. you the kind.
The house is about 1100 sq.ft. adn the installer put in a 100k boiler. My first thought was too big, but I was not there to point fingers only get facts.
The connected radiation is about 75' of a baseboard type emmiter. But there is no information I can find. It is fin tube, 1/2" has 1 1/4" opeining on the bottom and top with a louvre to control air flow. but it is sunk in the wall and not surface mounted like a baseboard.
Any idea what the output would be? I am tempted to use the 600 btu/ft as it looks EXACTLY like a baseboard, but if it is a convector adn has different outputs I do not want to give the wrong info.
Sorry there is no picture as the digital cam is in the shop.
Thanks all.
M0 -
Thanks Brad
I guesstinates the radiation at no more than about 40k..everyoine else is " no that should be good size for the boiler, but not ONE!! measured the radiation!! No heat loss...total frustration.
they added an additional grand of accessoris to try and fix it..and gee...no improvement..go figure0 -
You could be coy and tell the Owners
that what they really need is much more house.
I share your pain.0 -
with 1/2\" radiation,
You likely won't even use that much heat if it is all on one continuous loop.
Noel0 -
it is
nuff said.
the installation itself is nice and clean, ggod soldering, straight lines, but it was a guy that has been "doin this for 40 years..." no pumping away, and a few other "newfangled ideas" he has no use for....
oh well..I will submit my report, and then let them hash it out0 -
I like Brad's analogy, Tim
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements