PEX for Base board hot water
JOE_99
JOE_99 Member Posts: 15
I want to use Pex with oxygen barrier in my BBHW system and some copper.What type of PEX should I use.I'm not sure yet if I will use 180 or 150 degree water.Can you use PEX at the higher temp.Have only seen Pex rated at 200 degrees.
  • Mitch_5
    Mitch_5 Member Posts: 102
    pex ratings
    are temperature and pressure related.
    We have been using pex for almost 15 years on heat and have only had two problems.
    One was a boiler that ran away (electrician wired it wrong) and the safety did not go off so the pex melted and acted as a pressure relief.
    The other is the change by one manufacture from metric to standard eliminating availability of fittings for a retro fit. Same can be said for incompatibility of some rare brands.
    Veiga pextron and fosta pex work great.
    Mitch S.
    hot_rod Member Posts: 26,594
    Pex is commonly used
    for HWBB. I'd also suggest a PAP or the Viega FostaPex. Crunch the load numbers, often times 5/8" diameter is plenty to handle most zones. Much much easier to handle opposed to 3/4".
    hot rod