single phase 208 condensor motor
Techman
Member Posts: 2,144
Hidy-Ho Neighbors,I agree with the 40+ years of experiance gentlemen. Cond fan motors have run caps not start caps .Start cap and/or run caps are in the start winding,and the start cap would have some sort of disconnecting device .Enjoy your day!
0
Comments
-
single phase 208 condensor motor
greetings professor i had the pleasure of meeting you at my Oil 2 graduation at wilson tech. heres my question a condensor fan was wired at work. the fan had three wires and clearly the start cap was to be wired in series on the "purple lead" however it was not. when it was tested the motor would start after a push by hand. I suspected that the start cap was not in series and when the motor was spun the centrivical switch made and the motor ran. i am however smart enough to keep my mouth shut when there is a risk of flying tools! the solution was to go to the control panel and jump a hot lead from a contactor to the cap to solve the start up problem. now for my questions: was a start cap turned into a run cap? is the cap at greater risk of burnout? is the motor in any danger?
Thanks Michael R Siena0 -
The Push
The push you gave the motor was serving the purpose of the start winding. The start winding gives the motor the imbalancein magnetic field that is needed to start the motor. Once the motor is close to operating speed, the centrifugal force pushes the contacts on the centrifugal switch open to remove the start winding from the circuit.
From your post, it seems that the start winding circuit was not complete, so you stepped in to give it some help.
As far as your question goes, it appears that the jumper wire was used to simply complete the circuit through the start winding. Your start capacitor should still operate as a start capacitor. In the event the start capacitor is remaining in the circuit all the time, you will be overheating your start winding as it too will be in the active circuit all the time.
It was great meeting you at Wilson Tech.0 -
Mike
In 40+ years I don't think I have ever seen a split phase or capacitor start induction run motor used to drive a condenser fan. Condenser fan motors are usually shaded pole, PSC(permenent split capacitor) or three phase. I suspect the motor you are testing is PSC. PSC motors do not have a starting switch. Psc motors have a run capacitor that is wired in series with the start winding and is in parallel with the run winding. If it is disconnected it will act as you describe.Is the capacitor round black plastic or a gray or silver metal can? Is the Mfd. rating of the capacitor approximately 10 Mfd or much larger? What is the voltage rating on the capacitor?0 -
Thought this would help....
Amendment,...I thought there was some PSC info on fans before I threw this doc on the screen,...Sorry,.
MIke T.0 -
all three diags in the doc are for the compressor, not the fan!!
you can add my 40+ experiance to the above ones - also 9 to 1 odds its the fan motor thats bad not the run cap0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements