water source heat pumps

does anyone know what the course entails? is it basic or advanced? i havent been able to get through to the RPA.

Comments

  • water source heat pumps and cooling towers

    Does any one know of any good trade references for maintaining water source heat pumps and cooling towers?
  • RJ_4
    RJ_4 Member Posts: 484
    heat pumps

    (1) Each heat pump should have a flow switch, a wye strainer and a circut setter.
    (2)Loop temp. should be between 75 to 78 degrees.
    (3)Make sure you have some type of Boiler by-pass or primary secondary system to keep boiler temp. above 140 degrees. Bell&Gosset has a good piping diagram.
    (4)Set flow rate at 3gpm per ton.
    (5)Water treatment- Treat sump of tower(fluid cooler) with algaecide and scale inhibitor. (get a water teatment company).
    (6)Control of loop temp. is accomplished by cycling tower spray pump,fans(reccomend a VFD). and the boiler.There is propably a new contol on the market as we speak. Try a company called HEAT TIMER.
    (7)Check with the tower manufacturer for P/M.
    (8)Keep the loop temp. at 75 and the air filters clean .

    There was an error rendering this rich post.

  • hot_rod
    hot_rod Member Posts: 23,405
    Tune in for Mr. Eathertons online heat pump seminar, 6/6

    details at www.radiantpanelassociation.com. This Wed.

    I'm sure you will learn a lot about hp's and installation tips.

    hot rod
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mtfallsmikey
    mtfallsmikey Member Posts: 765
    Can't stress water treatment and filtration enough

    Especially if you are in an area with lots of new construstion, dust, (and an international airport nearby like I have!). According to one water treatment company here in the D.C. area, the most common foreign matter that winds up in towers in the downtown area the most is brake pad/shoe dust! Cooling towers are very efficient air scrubbers! A plate-type HX, mainstream/sidestream centrifugal separator will go a long way to prevent fouling. And, check with your water treatment co. about using a dispersant along with the rest of the chemical mix.
  • singh
    singh Member Posts: 866
    closed loops

    eliminate the filtration and treatment and wye strainers and flow meters etc....
    annual maintenance should check the glycol % in a closed loop.


    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Can't wait!

    We've got four systems in the pipeline. Two that incorporate radiant + A/C, one with radiant, A/C & solar (both PV and hydronic) & one that is strictly air.

    Another exciting chapter in the book of mechanical contracting.

    I'm planning on being a sponge during ME's presentation tonight.

  • don_192
    don_192 Member Posts: 45
    I hope

    the teacher gets into dx geo system as well.Check the efficency of the dx geo verse the water geo.You'll be surpise.

    No waterside issue to even worry about.
  • Brent_2
    Brent_2 Member Posts: 81
    water source heat pump

    Every water source (boiler/tower) heat pump job I have been involved with has been designed for 70° for winter and 90° in summer.