water source heat pumps
does anyone know what the course entails? is it basic or advanced? i havent been able to get through to the RPA.
0
Comments
-
water source heat pumps and cooling towers
Does any one know of any good trade references for maintaining water source heat pumps and cooling towers?0 -
heat pumps
(1) Each heat pump should have a flow switch, a wye strainer and a circut setter.
(2)Loop temp. should be between 75 to 78 degrees.
(3)Make sure you have some type of Boiler by-pass or primary secondary system to keep boiler temp. above 140 degrees. Bell&Gosset has a good piping diagram.
(4)Set flow rate at 3gpm per ton.
(5)Water treatment- Treat sump of tower(fluid cooler) with algaecide and scale inhibitor. (get a water teatment company).
(6)Control of loop temp. is accomplished by cycling tower spray pump,fans(reccomend a VFD). and the boiler.There is propably a new contol on the market as we speak. Try a company called HEAT TIMER.
(7)Check with the tower manufacturer for P/M.
(8)Keep the loop temp. at 75 and the air filters clean .There was an error rendering this rich post.
0 -
Tune in for Mr. Eathertons online heat pump seminar, 6/6
details at www.radiantpanelassociation.com. This Wed.
I'm sure you will learn a lot about hp's and installation tips.
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Can't stress water treatment and filtration enough
Especially if you are in an area with lots of new construstion, dust, (and an international airport nearby like I have!). According to one water treatment company here in the D.C. area, the most common foreign matter that winds up in towers in the downtown area the most is brake pad/shoe dust! Cooling towers are very efficient air scrubbers! A plate-type HX, mainstream/sidestream centrifugal separator will go a long way to prevent fouling. And, check with your water treatment co. about using a dispersant along with the rest of the chemical mix.0 -
closed loops
eliminate the filtration and treatment and wye strainers and flow meters etc....
annual maintenance should check the glycol % in a closed loop.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Can't wait!
We've got four systems in the pipeline. Two that incorporate radiant + A/C, one with radiant, A/C & solar (both PV and hydronic) & one that is strictly air.
Another exciting chapter in the book of mechanical contracting.
I'm planning on being a sponge during ME's presentation tonight.
0 -
I hope
the teacher gets into dx geo system as well.Check the efficency of the dx geo verse the water geo.You'll be surpise.
No waterside issue to even worry about.0 -
water source heat pump
Every water source (boiler/tower) heat pump job I have been involved with has been designed for 70° for winter and 90° in summer.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements