Radiant Heat with Carpet
Tom Hopkins
Member Posts: 554
I believe the RPA has done some research and notes the "R" value of a plethora of carpet/underlayment conditions.
However, common sense is a great general design parameter. The greater the "R" value of the material the energy must pass thru (sub-flooring, flooring, pad, carpet, throw rugs, etc.) the higher the water temperature must be in the tubing to make it to the surface of the top layer.
In all cases, the lower the water temp can be, the better. At some point, the cost to make the water 180 or above - to meet the BTU output of the radiant system needed - will exeed design physical limits, never mind destroy any benefits a decent mod-con can achieve, by virtue of them requiring under 160F water temps to achieve the highest level of efficiency.
If efficiency is NOT a consideration, running water at 240F could probably make surface temps around 85-90 (the practical design limit of surface temps desired in a radiantly heated room,) even with a 3/4" sub-floor, 3/4" hardwood top, 5/8" underlayment, and 1" tall carpet!
Unfortunately, it would take a day of 240F water passing thru to penetrate the "thickness" and R-value of such a floor.
If a 4" concrete slam with tubing in situ is trhe best of the best radiant method, the worst case scenario above would be the worst of the worst scenarios.
Does that help?
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=504&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
However, common sense is a great general design parameter. The greater the "R" value of the material the energy must pass thru (sub-flooring, flooring, pad, carpet, throw rugs, etc.) the higher the water temperature must be in the tubing to make it to the surface of the top layer.
In all cases, the lower the water temp can be, the better. At some point, the cost to make the water 180 or above - to meet the BTU output of the radiant system needed - will exeed design physical limits, never mind destroy any benefits a decent mod-con can achieve, by virtue of them requiring under 160F water temps to achieve the highest level of efficiency.
If efficiency is NOT a consideration, running water at 240F could probably make surface temps around 85-90 (the practical design limit of surface temps desired in a radiantly heated room,) even with a 3/4" sub-floor, 3/4" hardwood top, 5/8" underlayment, and 1" tall carpet!
Unfortunately, it would take a day of 240F water passing thru to penetrate the "thickness" and R-value of such a floor.
If a 4" concrete slam with tubing in situ is trhe best of the best radiant method, the worst case scenario above would be the worst of the worst scenarios.
Does that help?
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=504&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Radiant Heat with Carpet?
I am building new house and I would like to know if I can use carpet in the upstairs? If so, should I use a rubber pad instead of the foam pad? The down stairs will be tile & Kahrs wood flooring. All the bathrooms will be tile.
Granite Stater
0 -
carpet upstairs
Why not a radiant ceiling?0 -
The carpet everything mindset was borne
From cold floors but carpets are unhealthy period!!! From carpet mites, pet flees, mold, to out-gassing of the chemicals in them especially when heated
In a radiant house carpets are limited to pad sized ones, in baths, by entry doors, between beds, and runners in upper hallways for quietness thats it!!!
If you absolutely must do carpet then, save your money , do panel or cast iron radiators , you can pipe them off a radiant manifold with pex home runs as well
And you can run them on the same water temp as the rest of the houses radiant for cast iron it will typlically have to be ½ larger in surface area though - yes - a cast iron radiator that visible to all in the room works well at 120F and even below
0 -
Two thumbs down to radiant and carpet
from this installer.
First off look at the btu load for those rooms. Then determine the supply temperatures needed to meet that load on design day.
I'd caution against any temperature above 130 against plywood or the other subfloor products. I believe 140F is the max that plywood manufactures like to see for extended periods.
I would also look into panel rads, baseboard, ceiling and or wall radiant, before scorched carpet All these would be much more responsive and allow setback operation.
What about hardwood and area rugs?
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
been doing it for years
I have it in my home in 3 different bedrooms, 3 different types of carpet with climate panel, running straight out of my boiler controlled by indoor outdoor reset.
Been designing for it also but let the computer software be my guiding force. Sometimes, we can't get enough heat out and have to use supplemental heat i.e. walls.
I had to do that in my family room.
So far, 4 seasons later, everything seems to be ok.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements