ohm resistance
mike glass
Member Posts: 53
Hey Wallies! Does anyone know what the resistance in ohms between "hot" and neutral on a one hp pump should be (in what range)? The motor manufacturer's tech department asked me what an ohm was when I called! The reading presently is .7ohms.
0
Comments
-
Depends one what type of motor?,...
Ac sync, dc brushless, etc...
Why do you ask?0 -
potential short - check amperage
I just had occassion to have to check out some UP 26- 99F 1/6hp pumps. The factor said the 115V version should have 14 ohms.
If you really have such a low ohm reading, .7 ohms? then your amperage should be off the charts. Check your amperage draw against the rating of the motor. You may have some shorted windings.0 -
does it run?
What happens when power is applied?? .07 ohm should be blowing the breaker? If your motor runs then amp it out. J.Lockard0 -
.7 Ohms ???
Mike,
Are you sure that you are reading the meter on the correct scale? I'm not being a smart a--, but just a thought.
Also, what is the motor doing, or not doing?
Ed Carey0 -
If it's split windings with a centrifugal switch he may be reading the average between the start winding and the run winding if he's only got two leads. The start usually has a pretty low resistance and draws a lot of amps momentarily until it's switched out of the circuit. If the motor is not running then the switch is closed and the start winding is in the circuit.
And to answer the question, no I don't0 -
Thanks Guys! Sorry but I've been away from my computer due to work. I haven't installed this pump yet because it checks out like the previous new pump/motor combination which smoked as soon as power was applied! The voltage is correct coming to the leads and the pump company replaced (supposedly) under warranty but I want to make sure they don't have a "bad run" of these motors. I don't like being a "parts changer" but can't seem to get info from the motor manufacturer. Thanks, Mike0 -
centrifugal switch
Oh, and yes it has a centrifugal switch.0 -
Thanks MPF! You affirmed what I suspected and after installing replacement everything started and amped out OK!Thanks for the input! Mike0 -
Differnt meters give different readings also. There are good meters and cheap ones.0 -
You're welcome...
I'm glad it all worked out!0 -
ohms AC
You have to be a little careful with ohm readings and AC and inductive loads like a motor or tfmr or relay coil. The real ohms is Xl or inductive reactance. As the other post suggested the thing is to clip amp it when it's running. The ohm reading is useful to know to compare it to other motors for a quick test. Testing from hot or N to motor case is good too, shows that the winding or other wire connections aren't grounded.0 -
You know
I have evolved to realize that some times, changing parts is the cheapest, most definitive, and easiest thing to do.
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements