"Ugly's Electrical References". Your Q:,...Volts divided by amps on the name plate will give you the Impedance or Ohms. Z = E divided by I or Volts divided by amps = Ohm's. A 1 hp motor @ 115 vac FLA = 16 amps. A 1 HP motor @ 208 vac = 8.8 amps.
Your .7 amps are like you said basically a short. Cycle the motor with your clamp on amp probe on it and you can see what is happening. It will probably trip the breaker.
My .02
Mike T.
My .02
Mike T.
resistance
Hey Wallies! Does anyone know what the resistance value in ohms should be between the "hot" and neutral on a 1 hp pump motor? I am reading .7 ohms after the configuration (diagram)on the nameplate of the WEG motor for low voltage (115/208-230) and find the resistance too close to a short to be comfortable. Anyone out there know? The WEG factory tech person asked me what an ohm was! Thanks, Mike0 -
Check amperage also - sounds like problem
I just had a situation where we had to check out some Grundfos UP26-99 115V pumps. It's a 1/6th hp pump 2.15 Amp . The ohm reading was supposed to be 15. I believe the 230V model ws supposed to be around 235 ohms.
Check you amperage draw. There should be a rating on the motor. If it is significantly higer than the plate, you obvioulsly have a problem which might be indicitive of some shorted motor windings.0