A/c freeze up
        
            Options        
            
        
 
            
                
                    Eugene Silberstein 3                
                
                    Member Posts: 1,380                
            
                        
            
                    Do you have the temperature at the inlet of the compressor?                
                0                
            Comments
- 
            A/c freeze up
 Service Call;
 2 1/1 ton ac
 superheat ranging from 3-8 (13 req.)
 unit freezes up
 od amb:70
 id amb:58 wb/72db
 high side: 180psi
 low side: 55psi
 lat: 52
 delta p across coil: .24
 I tried adusting ref. charge but my suction pressure went way low, readusted back to how I found it. I think that air flow isnt an issue. This is fixed orifice. Is this a restriction issue?0
- 
            A couple of Quick Things
 You asked if there is a restriction issue. The answer is NO. Why you ask?
 If you had a restriction, you would be underfeeding the evaporator coil and your superheat would be higher than desired. In this case, your superheat is low.
 Low superheat is one indication of reduced airflow through the evaporator coil. How do you know that there is not an airflow problem? What have you done to check this?
 One other thing to consider is that your outside ambient temperature is 70 degrees and your indoor ambient temperature is 72. Your evaporator coil is very likely to freeze given that under those conditions, the system is actually too efficient.
 To verify this, grab the following set of readings:
 Evaporator saturation temperature.
 Evaporator outlet temperature.
 Condenser saturation temperature.
 Condenser outlet temperature.
 Compressor inlet temperature.
 Compressor amperage draw (actual, not nameplate).
 Voltage supplied to the compressor (actual, not nameplate).
 Give me these pieces of information and we'll all have some fun with it.
 0
- 
            freeze up
 evap sat. temp 30
 evap outlet temp 35
 cond sat temp 95
 cond outlet temp 75
 doesnt the delta t of 18 and lat 52 along with .24 press. drop through the coil indicate enough air flow?0
This discussion has been closed.
            Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 118 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 112 Geothermal
- 164 Indoor-Air Quality
- 3.7K Oil Heating
- 73 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements