Pressure Regulator Whats Wrong?

Hi, I installed a watts pressure regulator and it seemed perfect the model is the N45B-M1, didn't seem like anything too too tough, but it worked great. It turned my 150psi water down to 55psi. Worked super, then I left it and came home and found the pressure had crept back up to 130 and as soon as I runa facuet it came back down, but of course the initial burst is still there. This went right from a water meter into it, and then out. Thank you very much
Chris

Comments

  • Ray Landry_2
    Ray Landry_2 Member Posts: 114


    Chris it sounds like you need to install a potable water expansion tank at the cold inlet to your hot water heater. Now that the PRV is installed it acts like a check valve and doesnt allow the water to espand when heated, thus raising your systems pressure.
  • Empire_2
    Empire_2 Member Posts: 2,340
    Nice job Ray

    Just another tip, The tank air side diaphram has to be set @ the regulated pressure. Many different sized to choose from.

    Mike T.
  • Cosmo_3
    Cosmo_3 Member Posts: 845
    Things to check

    Ray had a good post, if in fact you installed on a water supply system that has a domestic water heater yes, you need a properly sized expansion tank, and as was mentioned make sure to increase the pressure in the air bladder of the expansion tank to the same psi as your regulated water pressure.

    Another thing to check is for debris that might have gotten stuck in the regulator. I believe the model you mentioned has a double union so that removal is easy (that is if you have isolating valves!), it is worth a look see. I had a couple of regulators, and backflow preventers not work because of "junk" getting in the way...


    Cosmo Valavanis
  • Chris Williams_4
    Chris Williams_4 Member Posts: 4


    Thank you VERY much, its funny when I called Watts they said that it was 99% chance that I wouldnt need the tank you suggested. I decided to take your advice since it made sense, and I am sure no surprise to you, you were absolutely right and it seems that my pressure problems are gone and I only needed to spend $35 to add this tank and clearly this house always needed it since the h20 heater press relief was weeping quite a bit. Thank you VERY VERY MUCH for your help a week of a lot of frustration appears to be at an end. Thank you
  • JK_4
    JK_4 Member Posts: 35
    Still needed

    The tank would not have worked without the pressure regulator so don't think that it was a waste. Just wanted to you feel better about the money spent.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Jerry_15
    Jerry_15 Member Posts: 379


    All right on advice, and glad it's fixed, but I have had brand new regulators creep without the hot water even on. Yeah, they replaced it for free, but what a pain.
  • that's strange

    My watts rep in chicagoland area always recommeded exp tank with any back flo preventor or pressure reducing device on ANY heating vessels....