Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
CMR 4.00 (venting question)

Al Letellier_9
Member Posts: 929
Here in Maine the total square inches (inside the flue liner) msut be equal to the TOTAL area of ALL flues connecting to it.....result: BIG CHIMNIES for multiple units
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=248&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=248&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Venting multiple oil burners
I have a formula for sizing multiple gas units to a single chimney. What do we use for sizing multiple oil burners using a single chimney. would it be the same?0 -
BTU
For oil you want to use the max btu input rating not what is is set to fire.0
This discussion has been closed.
Categories
- All Categories
- 87.1K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 58 Biomass
- 427 Carbon Monoxide Awareness
- 115 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 111 Geothermal
- 163 Indoor-Air Quality
- 3.7K Oil Heating
- 72 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 55 Water Quality
- 49 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements