Radiator plug removal

Again, while not fun to either do or to bleed, you could drill and tap each of those sections for an air bleeder. Since the top removes you could "hide" them towards the inside.

Comments

  • Chuck_17
    Chuck_17 Member Posts: 145
    Plug removal/venting

    See attached radiator. The client wants to use it in a bldg. with hot water heat. It looks like it was previously used for a one pipe system. Assuming the plug (on the end in the picture)has never been removed, do you think it will come out?
    This brings up another point - how was this radiator vented?
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928
    Bundy Rads Again

    Believe they're only suitable for steam as the tops of those looped tubes don't connect. Maybe (but highly doubtful) that each of those loops connects into the base in such a way to put them in series.

    Possible (but not really practical) to tap in an air bleeder very near the top of EACH looped tube...

    The old plugs usually do come out even if you do have to drill, cut and or other time-consuming things.

  • Steamhead
    Steamhead Member Posts: 17,380
    Chuck, these particular Bundys

    were never designed for hot-water heat. It might be possible to drill and tap each loop, but the water would not flow thru them properly.

    Best bet is to sell or trade them for ones designed for hot-water. Too late for Mad Dog's house- he already has Bundys- but you might find another steam afictionado who will want them.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Rodney Summers
    Rodney Summers Member Posts: 748
    Well,,,,,,

    Here's one idea that may work and work well.

    Rather than thinking about the unjoined tops of each section being a place to hide air, think about putting the system under a near vacuum before filling it.

    Even a mild vacuum would allow the "tubes" to fill some of the way up and allow normal migration of air in the upper rad sections to be caught in a boiler baffle or simple air separator - provided of course that you pump away from the PONPC - over time!

    Think about it. Even cast iron without water backing and circulation is an excellent heating "conductor."

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Chuck_17
    Chuck_17 Member Posts: 145


    Even steam must have had a problem with no vent?
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928


    Steam is lighter than air so it naturally rises to the top of each secion even when not connected across the top. The heavier air then exits via the vent. Remember--the air vent for a steam radiator is about 2/3 to 3/4 of the way DOWN.