Balanceing ???

Richard D.
Richard D. Member Posts: 32
I dont know if it ever worked right.I just got the customer and as you know most wont tell you it hasnt been working right lol..Been thinking of adding 2 flo checks.so we are on the same page with that one,,,.Thanks Rich

Comments

  • Richard D.
    Richard D. Member Posts: 32
    Balancing ?

    I have a split loop .Zone #1.. Taco Zone valves, (3).. when zone #2 or #3 call they pull thru the loop on zone #1..Cold to valve, it pulls thru 1 side of loop bypassing zone valve and continues back to boiler.. .#1 is the only split loop..piped correctly..only #1 heat when called for heat....Older system not sure how long it been doing it..Do you think balance valves would help??? Gate vales in system now... Thanks Rich
  • bob young
    bob young Member Posts: 2,177
    check it out

    balancing or gate valves will not stop ghost flow . if zone valves are shutting tight ,you might need a flow check on the opposite end of each loop. doid it ever work properly ?
  • bob young
    bob young Member Posts: 2,177
    check it out

    THE b.& g. vertical checks might be useful if it is a tight piping configuration. the horizontal pattern sometimes takes up space that is not available ! lol don't forget to include the engineering fee on your invoice.