Munchkin Condensate Tap

Garritt
Member Posts: 27
Just wanted everyone to know that on the older munchkin models the little hole in the condensate tap is there for a reason. Boss found a couple of munchkins with the breather hole covered up by the factory hose. Don't know if it was done by the install crew or by the factory, so double check, because if you don't, condensate will backup into the secondary/primary heat exchanger and will destroy the burner/ gaskets. Munchkin in the future is installing a "T" instead of the barbed coupler with the hole in it, so installers are not confused.