oil burner interfering with TV
Alan R. Mercurio_3
Member Posts: 1,624
Transformer or Ignitor?
You could be on the right track check to make sure you have proper grounding and make 100% sure the ignitor has a good ground to the burner housing
Your friend in the industry,<BR>Alan R. Mercurio<BR><BR><a href="http://oiltechtalk.com/discuss/index.php?sid=63c67a82829fdbdda388591b32998104">www.oiltechtalk.com</a>
You could be on the right track check to make sure you have proper grounding and make 100% sure the ignitor has a good ground to the burner housing
Your friend in the industry,<BR>Alan R. Mercurio<BR><BR><a href="http://oiltechtalk.com/discuss/index.php?sid=63c67a82829fdbdda388591b32998104">www.oiltechtalk.com</a>
There was an error rendering this rich post.
0
Comments
-
oil burner interfering with TV
I may be in the wrong forum, if so I apologize.
I have a beckett AFG burner that every time it lights their is interference on the customers TV. I was thinking it was the transformer ,but I'm not quite sure. Any help appreciated0 -
Before condemning the transformer,
Please let us know what the other controls on the system are. I've seen my share of contacts in "block type" controls cause this kind of interferance too.(just as they are about to make contact, there it is.Alan hit on the key point....GROUNDING. It has to be done properly on everything. Chris0 -
rf noise from an electronic igniter?0 -
one more
The list is pretty complete, check mechanical ground, not stressed enough, check grounding screw on electronic ignitor ususally an issue if a new ignitor is installed on an old plate, make sure good contact to buss bars, as Chris pointed out, aquastat block in MH controls can give you a problem, usually seen prior to burner starting and finally, if electronic ignitor, make sure power and neutral wires are connected correctly.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements