    Can anyone help me understand the equivalencies between a Hoffman 75 and a Gorton #2 main vent? In other words how many Hoffman 75s does it take to equal one Gorton #2?
  • Roughly

    2-1/2 Hoffman #75 vents to one Gorton #2, depending on what pressure you're measuring at.
  • Foreman
    Foreman Member Posts: 30


    My 75's are on the workbench, awaiting my #2's..cant wait to hear the air!
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,600
    When you get to the point

    where you can't hear the air you'll know that you've got it.
    Retired and loving it.
  • thfurnitureguy_4
    thfurnitureguy_4 Member Posts: 398


    real world: The Hoffman is like blowing thru a small tube on a the can of WD-40 the Gorton #2 is like blowing through an open piece of 1/2" pipe.