Ultra Piping question

hr
hr Member Posts: 6,106
should be sized to the flow rate it is required to move. If some secondaries can get enough BTUs with 3/4" pipe, really no reason to upsize.

What size Ultra do you have? The 80 and 105 can use a 1" primary loop. 155 and 230 1-1/4". The 310 1-1/2". That computes with the required flow, and is stated on page 15 of their installation manual.

hot rod

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=144&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • Mr Bill W.
    Mr Bill W. Member Posts: 10
    Ultra Piping question

    Is there any requirements or recommended size
    for the Primary Secondary connection.
    Piping off the boiler up to this point is 1 ¼ inch
    and the secondary loop is 1 ¼ and 1 inch Thought I might use a 3/4 inch PS connection
    Second item is on the length of the PS connection.
    Instructions say 12 inch max how crucial is this,
    is there any leeway
  • adambuild
    adambuild Member Posts: 414
    By the book!

    There can be no more than 12" between the T's and 1 1/4" is the best size for that connection.