Rebuild Lg. Taco flow-checks?

Saggs
Saggs Member Posts: 174
I've got a lg smith boiler w/ 2 taco black iron flow checks that are not stopping convection flow and are overheating the space. They're 1 1/2", The green ones. Can these be rebuilt or cleaned other than changing them out? It's an old steam system that had been converted to water and of course no shutoffs after the flow checks. Thx

Comments

  • Big Ed
    Big Ed Member Posts: 1,117
    Clean Flowvalves

    Why yes,it's very rare I find that they need to be changed.Clean the weight,seat and stem with a fine steel wool .
  • Saggs
    Saggs Member Posts: 174


    Thx Big Ed I'll try cleaning them up and install some new gaskets and packing seals. There really shouldn't be anything to "break".
  • Joe Mattiello
    Joe Mattiello Member Posts: 720
    they can be cleaned

    You can take the top assembly off for cleaning and reassemble them. For your reference I attached the instruction sheet.

    Taco, Inc.
    Joe Mattiello
    Technical Service Technician
    joemat@taco-hvac.com
    401-942-8000 X 484
    www.taco-hvac.com
    Joe Mattiello
    N. E. Regional Manger, Commercial Products
    Taco Comfort Solutions