Our 1922 one pipe low pressure steam system is getting an early Christmas present: A vaporstat to replace the pressuretrol, which is currently cranked down to 1/2 psi cut-in and 1 psi differential.
There are 2 vaporstat models: the L408A1157 has a 0 - 4 psi pressure range, and the L408A1132 has a 0 - 16 ounce/sq.in. range. Which one should I get?
I'm confused by Dan's discussion on page 14 of "The Lost Art of Steam Heating." He says to set a Pressuretrol to 1/2 psi cut in and 1 psi differential, but then he says if you have a Vaporstat, set it "to Cut In at about four ounces and Cut Out at about ten ounces."
But in the preceding discussion, he says the radiators need 1 psig to heat the house. And my piping losses are probably around 2 ounces (longest run is about 85'). So don't I need a cut out of 18 ounces/sq. in.? You can't set the 0 - 16 oz./sq/in. Vaporstat this high.
There are 2 vaporstat models: the L408A1157 has a 0 - 4 psi pressure range, and the L408A1132 has a 0 - 16 ounce/sq.in. range. Which one should I get?
I'm confused by Dan's discussion on page 14 of "The Lost Art of Steam Heating." He says to set a Pressuretrol to 1/2 psi cut in and 1 psi differential, but then he says if you have a Vaporstat, set it "to Cut In at about four ounces and Cut Out at about ten ounces."
But in the preceding discussion, he says the radiators need 1 psig to heat the house. And my piping losses are probably around 2 ounces (longest run is about 85'). So don't I need a cut out of 18 ounces/sq. in.? You can't set the 0 - 16 oz./sq/in. Vaporstat this high.
0
Comments
-
FWIW this is my thread on the same issue earlier this week:
http://forums.invision.net/Thread.cfm?CFApp=2&Thread_ID=29290&mc=60 -
Get the 1-PSI Vaporstat
If the house has had any insulation, storm windows, weatherstripping etc. added you don't even need 1 PSI at the rads. Ounces rule!0 -
go low
Hi Santa,
What a nice present for a steam system. Pick the 0-16 oz. and try to operate around 8 oz., that will be enough to heat the house.
Things to add to the Christmas list:
1) Lots of new vents with plenty of capacity. The system will need plenty of venting to keep the burner from cycling on the pressure control.
2) A professional burner tune-up to peak your efficiency and make sure you are not over-firing. Too much steam can also make the burner cycle on the pressure control.
3) A thermostat check up to make sure that it is set for your steam system. You want to avoid the t-stat cycling the burner during a call for heat.
Best regards and happy shopping, Pat0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements