hot air furnace problem
Paul@P.C. Htg.
Member Posts: 1
80% hot air furnace in atic. P.C. got wet. Changed p.c. board and flame sensor. Furnace has hot surface ignitor. Furnace goes through starting sequence and lights. Have full flame for approx. 3 or 4 seconds then shuts down. Retries to start 3 more times then shuts down. Panel light blinks 4 times indicating ignition failure check ground. We have checked ground and even tried another pc board. NEED HELP.
0
Comments
-
Make sure flame sensor is in contact with flame.0 -
Flame Failure
I would check these:
1. Polarity
2. Clean the flame sensor
3. Make sure the ceramic on the flame sensor is not cracked
4. Change the flame sensor wire. This circuit measure micro-amps in most systems. I have found flame sensor wires that appeared fine visually but were in fact causing a problem.
Good Luck! -DF
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Dry dry dry
Make sure the whole thing is dry. I mean all moisture gone. Check with micro amp meter, sounds like you are not getting any signal at all. You may have a very weak short that is canciling out you flame signal, but not tripping lo volt fuse...0 -
What make/model furnace? If its the ever popular Goodman, try running a peice of wire from FS right to board ( bypassing molex connector ).0 -
You still have moisture
somewhere. The boards see moisture as an AC signal on the sensing circuit and will not fire. I suggest taking everything apart and drying it out with a fan. How much moisture did you get? Reason I ask is that GAMA recommends replacing the entire unit if it has been under water, flooded, or soaked in any way. Homeowners insurance will usully cover it.
I have seen jobs that got wet and we chased them for several weeks until frustration set in - replaced unit problem goes away. It is not my usual way to do things as I like to fix things but .... sometimes you have no choice.0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements