Main steam vent placement
ktt
Member Posts: 3
> I have a single pipe steam heating system in a 3 <BR>
> floor brownstone with no mains. I've consulted <BR>
> with two plumbers and one recommends placing a <BR>
> hoffman #75 vent on the top floor at the end of <BR>
> the run (in my bedroom as a matter of fact). The <BR>
> other recommends placing the vent in the boiler <BR>
> room, gas fired, at the return piping. Having a <BR>
> vent in my hoffman #75 vent in my bedroom concens <BR>
> me for noise and humidity issues but I'm not sure <BR>
> puting the vent in the boiler room will work. <BR>
> Which options is better or correct?? <BR>
<BR>
> floor brownstone with no mains. I've consulted <BR>
> with two plumbers and one recommends placing a <BR>
> hoffman #75 vent on the top floor at the end of <BR>
> the run (in my bedroom as a matter of fact). The <BR>
> other recommends placing the vent in the boiler <BR>
> room, gas fired, at the return piping. Having a <BR>
> vent in my hoffman #75 vent in my bedroom concens <BR>
> me for noise and humidity issues but I'm not sure <BR>
> puting the vent in the boiler room will work. <BR>
> Which options is better or correct?? <BR>
<BR>
0
Comments
-
Main steam vent placement
I have a single pipe steam heating system in a 3 floor brownstone with no main vents. I've consulted with two plumbers and one recommends placing a hoffman #75 vent on the top floor at the top of the run (in my bedroom as a matter of fact). The other recommends placing the vent in the boiler room, gas fired, at the return piping. Having a vent in my in my bedroom concens me for noise and humidity issues but I'm not sure puting the vent in the boiler room will work. I have 1 1/4" vertical mains running a 25' with a 18' horizonatal run (2" pipe) from the boiler to the riser for a total run of approx. 33'. Which options is better or correct??0 -
Post the length and diameter of your mains. Someone will help.
OK, I see you edited your post. You have about .4 cu. ft. in your main. A Gorton No. 1 or Hoffman No. 75 would be sufficient to vent the main in the boiler room. If you vent the riser instead you may want to stay with a Hoffman No. 75 as I believe that vent closes against water, where the Gorton does not. Not sure of that but that is my recollection. Steamhead or any of the steam guys?0 -
Bump.0 -
Gortons do close against water
there are very few vents made today that don't. Either the Gorton #1 or Hoffman #75 is fine, but the Gorton is less expensive.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements