I need to lift low pressure condensate approximately 3 feet after the trap off of a steam to water heat exchanger. Usually you can lift condensate, without a pump if the control valve on the heat exchanger is two position. In this case we have a 1/3 2/3 control valve arrange, so that we have better control at low load conditions. Unfortunately, this does not allow you to lift condensate at low load conditions.
We want to give our owner two options, a condensate return station being the preferred. The owner mentioned a diaphram type device that will accomplish the lifting without a pump. Does anyone have experience with this device that could shed some light on operation, availability and cost?0 -
Is this already installed?
If so, is it not working?
With a modulating steam valve you won't lift the condensate at low load, but the condensate will build up in the coil and cripple the heating capacity. Once there is enough condensate/too little heat exchange surface because of the volume of condensate in the heat exchanger coil the steam valve will open more to admit more steam, then you will get condensate lift.
Am I missing something? Not recommended for steam heating coils with very cold air inlet temps, but this ain't that.0 -
Lift
I have battled this situation many times. I don't agree with Jim's solution, headaches. IMHO it's the lift station or a Sarco pumping trap. bob0 -
Jim
poor temperature control. bob0 -
Thanks
I did some research today and found the only way to accomplish this would be the pump-trap you mentioned. At low load, not only do we have poor temperature control, we don't have enough pressure to lift the condensate. We will recommend a condensate return station.
Thanks for your input.0
This discussion has been closed.
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 120 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 395 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements