need a dvise

David, first let me say it’s always nice to see your name come across the threads here. Good to see you my friend.

Depending on the type of expansion tank you may be right it may be installed incorrectly. The relief valve they sent you sounds like it’s for a water heater not a boiler. Send it back and let them know you’re not in the business of making rockets out of heating systems :)



Your friend in the industry,<BR>Alan R. Mercurio<BR><BR><a href="http://oiltechtalk.com/discuss/index.php?sid=63c67a82829fdbdda388591b32998104">www.oiltechtalk.com</a>

There was an error rendering this rich post.

Comments

  • This content has been removed.
  • This content has been removed.
  • jim lockard
    jim lockard Member Posts: 1,059
    hey David

    sounds like you have a relief valve for a water heater not a boiler. The 200,000 Btu rating is ok but your going to want a 30 pound relief so that the valve will open should the pressure exceeds 30 psi. Best Wishes J.Lockard