Pro Press with compressed air?

Don \"Grumpy\" Walsh
Member Posts: 184
Has anyone used pro press to install compressed air systems? I'm thinking of 125psi top pressure in the system. About 400 lineal feet of 1 1/4" main with 30 or so 1/2" drops. Has anyone used pro press for this application?
0
Comments
-
Yes we have done a to of it with no problem. If you read the ridgid web site it is approved for compressed air. There is however some stipulation on compressor oil.
ED0 -
I do it all the time. Rigid recommends that you use Type L copper and ProPress Gas fittings, as the O-rings in those fittings can stand up to the oils in the system.0 -
Done
Used Propress to make up some 2 inch copper (L) for air lines at a plant making trusses for houses and so far no problem. I called Ferguson and they provided the fittings and the spec sheets that made the designer/engineer happy. J.Lockard0 -
IMHO...
....it may be the best application for this product line. I've wanted to say this since I saw this post a couple a days ago ( and I know others have too , lol ).
Edit : thinking of the legal aspect of writings it's all a beautiful field of flowers you know. There is no bad product brother , it's all just good...perhaps beautiful depending on your perspective of the scene ( so on and so forth ).0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 939 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements