Who's right???
andy_21
Member Posts: 42
Getting estimates on a new Direct vent Gas fired cast iron w/ outdoor reset, heating system for 3000sq'2 1/2 bath new construction home.
1ST fl. Radiant w/Hydro air back up, 2 nd fl Hydroair& 60 gal Indirect domestic hot water w/ prority.
Did the slantfin heat loss program & came up w/ 73K @ 0 design.From everything I read here, do the heat loss & size boiler to largest load. The heating contractor & plumber I met with want to go 120-130K. They say you need to account for the Indirect w/ at least 40K btu.
What they way to go?
I've stayed w/ Cast iron type because of the Different temp set up that we have, so I don't think the Mod/Con would help. Any ideas?
1ST fl. Radiant w/Hydro air back up, 2 nd fl Hydroair& 60 gal Indirect domestic hot water w/ prority.
Did the slantfin heat loss program & came up w/ 73K @ 0 design.From everything I read here, do the heat loss & size boiler to largest load. The heating contractor & plumber I met with want to go 120-130K. They say you need to account for the Indirect w/ at least 40K btu.
What they way to go?
I've stayed w/ Cast iron type because of the Different temp set up that we have, so I don't think the Mod/Con would help. Any ideas?
0
Comments
-
Btu for Indirect
You do not have to account for the btu's for the indirect as you should be using a priority control thus making it irrelevant...0 -
thoughts
I would size the boiler for the heat load, unless there is a particularly high domestic hot water load. Short-cycling is a very common problem, and there is no reason to deliberately cause it. Obviously I am completely guessing, but for a typical new home, 24btu/sf is an over-estimate of the heat load. I think you will find that the actual load is less than that, depending on the design of the house. Lots of windows, particularly high ceilings, or lots of rooms with 3 exposed walls among other factors will affect the heat load significantly.
You can size air handlers for reduced temperatures also. It is worth looking at a mod/con, particularly with a direct vent application. The mod/cons have the advantage of being compact, wall-hung, and sealed combustion, even without the efficiency gains, which you can still take partial advantage of with hydro-air.
The Vitodens 200 or 100 would be excellent choices. They do not necessarily need to be connected to a Viessmann indirect. The Triangle Tube Prestige is also a nice choice with a competitive price, though the smallest version is the 110.0 -
Consider
sizing the Hydro coils for a lower temp to allow for condensation for a good portion of the time and go with the Mod/Con.You only pay for the coils once. If you require more DHW than the boiler can recover go with a larger indirect and/or operate indirect at 160 w/ a Tempering valve(which you should have anyway)I'd keep looking for contractors
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
All three distinquished colleages are correct
Your "contractors" are playing it safe and not doing the math. Will they be paying your heating bill every month?
A Mod Con should NOT be ruled out. You reallt should get some quotes from the pros here at Find a Professional....The Best in the Business.....MaD dog
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Yes.
> Getting estimates on a new Direct vent Gas fired
> cast iron w/ outdoor reset, heating system for
> 3000sq'2 1/2 bath new construction home. 1ST fl.
> Radiant w/Hydro air back up, 2 nd fl Hydroair&
> 60 gal Indirect domestic hot water w/
> prority. Did the slantfin heat loss program &
> came up w/ 73K @ 0 design.From everything I read
> here, do the heat loss & size boiler to largest
> load. The heating contractor & plumber I met with
> want to go 120-130K. They say you need to account
> for the Indirect w/ at least 40K btu. What they
> way to go? I've stayed w/ Cast iron type because
> of the Different temp set up that we have, so I
> don't think the Mod/Con would help. Any ideas?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Yes.
> Getting estimates on a new Direct vent Gas fired
> cast iron w/ outdoor reset, heating system for
> 3000sq'2 1/2 bath new construction home. 1ST fl.
> Radiant w/Hydro air back up, 2 nd fl Hydroair&
> 60 gal Indirect domestic hot water w/
> prority. Did the slantfin heat loss program &
> came up w/ 73K @ 0 design.From everything I read
> here, do the heat loss & size boiler to largest
> load. The heating contractor & plumber I met with
> want to go 120-130K. They say you need to account
> for the Indirect w/ at least 40K btu. What they
> way to go? I've stayed w/ Cast iron type because
> of the Different temp set up that we have, so I
> don't think the Mod/Con would help. Any ideas?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Yes.
What they have said already is quite true. Even your own heat load number seems high. I have a 2,800 sq ft 1906 two story 9 foot ceilings down, 8 ft up, and 700 sq ft of glass and my load is less than 50,000btu/hr at -4F. Oversized, misapplied boilers are hugely wasteful, wear out faster, and reduce comfort. Also, in several areas are against code. The one caveat for your installation is that I would increase the capacity some in order to make up for the typically 20% extra loss due to forced air ductwork.
Boilerpro
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements