Member Posts: 2,440
that your longest branch run will be? And what flow rate will you require?
My gut says, without knowing all the details, with a 0011 you should be able to get enough flow to any radiator within reason, even if your subject radiator is twice as far from the main as any other. The fact that you are using two monoflow tees reinforces this.
Remember that if you do not get full flow, -say you get only half-, you will still have about 90% of your output from that radiator.
To be more definitive, I would need more information. Distance between the fittings, runout length, target flow rate and number of elbows in that branch circuit.
mono-flow
Is there a simple way to determine how far a radiator can be located from a 1 1/4" main mono-flow loop if I install both a supply and return momo-flow tee. the main loop is 140 feet and there is a taco 0011 circulator. there are 9 radiators on the loop each installed with isolation ball valves.0