sizing hot water systems for nursing homes
Options
kevin miller
Member Posts: 1
I stumbled onto a formula to size domestic hot water systems for nursing homes, quite by accident I might add. This is for upright gas fired boilers, although it may work for other boilers I have not done any calcs. on others. This formula is for facilities with a laundry and dietary dept figured into the equation.
First take the total number of beds and multiply by 12,000 btu, then multiply the number of beds by 3 to get the gals. of hot water storage needed. An example would be a 100 bed facility would need 1,2000,000 total btu's and 300 gals. of hot water storage. The btu and gals I used are on the high end, you could use a lower number like 11,000 and 2 gal per bed. I prefer to use the higher number as well as an extra boiler in the bank to create a redundancy factor for boiler failures and service shutdown times.
When called to troubleshoot hot water shortages or designing a system you can use this formula as a quick reference to see if the system is at least in the ballpark.
I hope this will be usefull to someone out there.
First take the total number of beds and multiply by 12,000 btu, then multiply the number of beds by 3 to get the gals. of hot water storage needed. An example would be a 100 bed facility would need 1,2000,000 total btu's and 300 gals. of hot water storage. The btu and gals I used are on the high end, you could use a lower number like 11,000 and 2 gal per bed. I prefer to use the higher number as well as an extra boiler in the bank to create a redundancy factor for boiler failures and service shutdown times.
When called to troubleshoot hot water shortages or designing a system you can use this formula as a quick reference to see if the system is at least in the ballpark.
I hope this will be usefull to someone out there.
0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements